It is currently Sat May 03, 2025 7:26 pm
PostPosted: Mon Jun 18, 2012 4:48 pm
Thanks guys. I would bet that if most looked, the feed to your panel from the meter base would be aluminum. Although, it may not be superior to copper, I honestly can't afford to run copper the 150' to the garage. :(
PostPosted: Mon Jun 18, 2012 10:38 pm
I believe the fire issues were partly due to incorrectly sizing the aluminum and copper the same.
Aluminum is not as conductive as copper, so generally speaking if a circuit was to call for a 4 gauge COPPER wire, you would want to use a 2 gauge Aluminum in its place to assure adequate conductivity
PostPosted: Mon Jun 18, 2012 10:42 pm
Cody, the NEC is clear about what size the conductor should be, based on material, and in general, the inspectors enforced that. Generally, the fires were started by heat at the terminations. If you undersize any wire by 2 gauge numbers, copper or aluminum, it won't get hot enough to start a fire.
PostPosted: Mon Jun 18, 2012 10:50 pm
Cody, the NEC is clear about what size the conductor should be, based on material. The fires were started by heat at the terminations.
Not that I have ever personally witnessed an aluminum wire fire, I was told/taught (In State of MN certified contractor continuing ed) that excess heat (from undersized wires) also played a roll?
Connections were mentioned as well, but the wire size thing stuck in my mind as much as connections/corrosion.
*disclaimer.. I am a carpenter, and only play an electrician on tv*
PostPosted: Mon Jun 18, 2012 10:56 pm
doesn't the load placed on the circuit play a roll? Meaning, if a circuit at its limit and has (even slightly) undersized wire, isn't the "potential" there for overheating of that wire to the point of being a fire hazzard?
PostPosted: Mon Jun 18, 2012 11:47 pm
oxford wrote:
In the panel at the house the grounds and neutrals are all connected to the same busses. 2 hot legs and one bare wire run down from the meter base, bare wire goes to the ground/neutral buss. I then have a separate ground wire that runs from the ground/netural buss to my water main that comes into the house. From what I see the grounds and neutrals are not separated from, each other.
That is correct, at that point they are connected together...
oxford wrote:
Now to the sub panel. Are you saying that the grounds and neutrals do indeed need to be on separate busses in that panel and then running back to the main panel?
Yes, in the situation you describe, they are supposed to be separate...
oxford wrote:
What is the difference when they get to the main panel and essentially go to the same thing or do each of those wires not get hooked up to the ground/neutral buss that is in there?
Remember that inside a house "Ground" and "Neutral" aren't the always same thing... A "Ground" wire should never be carring current but a "Neutral" can.
oxford wrote:
Also does the water line I have running out to the garage make any sort of difference or not? Thanks.
Yes it does.... If there were no metallic connection between the two buildings the NEC would allow you to run only three conductors (two hot and a neutral) between the two buildings and a "ground" wire run to a copper ground rod driven into the ground.... (It would be wired just like the main panel)
I think the reason why the NEC won't allow you to ground to the water line in both places is so there is no way to accidently get current flowing through the water line
PostPosted: Tue Jun 19, 2012 4:40 pm
Thanks Bobby-S, 2 separate wires it is.
PostPosted: Tue Jun 19, 2012 8:04 pm
If I could get a deal on copper, is 3 individual pieces of 2 ga. THHN and 1 4 ga. in pvc underground ok to use for the feeders?
PostPosted: Tue Jun 19, 2012 9:27 pm
It has be at least 75deg C wire not 60deg C. Number 6 will work for the ground.
PostPosted: Wed Jun 20, 2012 8:23 am
The breaker is the current limiter. The NEC specifies wire sizes with plenty of safety factor for that limit. For a 20A circuit, you have to use #12 wire to meet code, but if you run a 20A load on a #14 extension cord, you'll find it might get slightly warm to the touch.
But if there's a fire from aluminum wiring, everything causing heat, even a little, contributed. If some guy installed aluminum wire and didn't use the right connectors and anti-corrosion grease, and used the copper sizing table instead of the one for aluminum, and the inspector was so bad he didn't notice any of this, then there are a lot of contributing causes of the fire. :lol: